| | In regards to your Question #1 above, I have never heard of nor can I imagine a Data Center that does not have any AC powered equipment, Perhaps I am missing something here, but could you describe a situation where one might find such a DC? Thanks
Richard S. Anderson, RCDD CSI CDT http://www.servamatic.net |
| | | | Forum Member
       
Group: Forum Members Last Login: Monday, October 10, 2011 1:34 PM Posts: 30, Visits: 78 |
| | Granted at some point all DCs will have AC powered equipment, but not in all metal server cabinets or racks. I recently toured a renovated DC facility that leases around 100,00 square feet of unoccupied, raised floor, colocation space that had less than 500 square-feet occupied by racks/cabinets containing AC powered equipment and many of the racks were used for cable termination and did not contain any powered equipment. The owners intent is to populate the rest of the facility by leasing space. This particular DC was once an AT&T DC and has a grounding grid throughout under the raised floor, the raised floor grid is bonded to ground. As racks / cabinets are added they are bonded to the grounding grid. The PE I spoke with does not believe that a grounding grid is necessary in a DC and is just a waste of money and insists that the only grounding required by code in a DC is the AC power cord grounds. So what happens if a 208 or 480 V cord power cord is damaged and comes into contact with a cabinet that is not bonded to ground without tripping the breaker? If this cabinet is bonded by a cable tray or metal floor grid to other cabinets then someone touching any of the cabinets could be shocked. While the probability of this happening is remote it could happen. The point and question is do metallic racks. cabinets, floor grid, telecom conduits, etc that are not used to house AC equipment in a DC required to be bonded to ground? I work for a hospital and my interpretation of NEC has been and still is that anything metal you put into a building that has the potential for conducting electricty and is exposed to someone touching it (maintence workers or the public) should be bonded to ground. In reality I have been doing this many years and rarely see it enforced. It seems the Code is open to interpretation. Also, many well designed DCs use consistent cabinets that are independent of the equipment they may house. The equipment can change with time and may not always be powered equipment, such as copper patch panels and fiber termination hardware. I am being told by a PE that none of the cabinets in a DC need to be bonded to ground without any distinction between cabinets with powered equipment or passive cabinets. Also someone made the point that fax machines and copiers don't need to be boded to ground even though they are consdidered IT equipment. That really doesn't hold water. Most copiers / faxes I have used have a plastic cabinet that isolates the internal metal from human contact. The internal metal is bonded to ground through the power cord and there is no potential for the cabinet to become energized from a faulted circuit. This is different than a metal server cabinet in a DC that may become energized from a faulted circuit via cable tray floor grid or other metal conductor. |
| | | | Forum Guru
       
Group: Forum Members Last Login: Sunday, February 14, 2010 10:27 PM Posts: 59, Visits: 249 |
| FL-RCDD (1/26/2010) The PE I spoke with does not believe that a grounding grid is necessary in a DC and is just a waste of money and insists that the only grounding required by code in a DC is the AC power cord grounds. . The PE is exactly correct, but yopu do not quite understand what he is saying.FL-RCDD (1/26/2010) So what happens if a 208 or 480 V cord power cord is damaged and comes into contact with a cabinet that is not bonded to ground without tripping the breaker? .This is where I think you get lost and did not fully understand what the PE is saying. From NEC 250.2 requires all metal objects likely to come in contact must be bonded. This is where items like cable racks fall under. But let's go to something basic like a equipment lineups. Assuming there is AC powered in the equipment rack, means an AC circuit is ran to it. Per code there is an EGC ran with the branch ciruit. Many of the equipment racks have more than one AC circuit in them. Most use at least use 2 from a UPS for redundancy. Ok the next rak is installed next to the rack we just talked about. It is bolted to the adjacent frame, and has its 1 to 4 AC branch ciruits ran to it with each circuit having an EGC. Ok now we a a line up with several equipment racks, and a lot of AC branch circuits with lots of EGC to form one massive ground plane. Adding a supplemental ground would add no value at all except to the contractors bank account. This is what the PE is telling you. So you ask what happens if a 208 or 480 volt line came into contact with the line-up. Well first thing the voltage is not 208 or 480. Those are phase to phase voltages. Phase to ground is 120 and 277 volts. Anyway the fuse or circuit breaker would operate immediately like it is suppose too. It has dozens of EGC's providing the plannned fault path. Moving onto cable racks, well that is classified as a raceway, and NEC Article 392 covers cable trays. Guess what? They have to be bonded or th emis used term grounded. 392.7 states cable trays must be grounded per NEC 250. NEC 250 tells you that any enclosure shall be grounded and sized to to clear any fault likely imposed on it. That leads you to NEC 260.122 for the size of the bonding conduct. The size is determined by the size of the circuit breaker size of the largest circuit likely to be encountered. If you are looking for a 1-size fits all, then a # 6 AWG should do the trick as it will clear a 200 amp breaker safely and quickly. Hope that helps
DereckC MSEE, PEModerator Mike Holt Code Forum |
| | | | Forum Member
       
Group: Forum Members Last Login: Monday, October 10, 2011 1:34 PM Posts: 30, Visits: 78 |
| | Dereckc, MSEE PE Thanks for your comments. I understand that technically 208 and 480 may not be the exact correct voltages. It has been a long time since I took three-phase power classe and it is irrelevant anyway in the discussion. I will be sure to let the PE, electricians, our DC manager and multiple manufacturers of UPS and computer room PDUs that they are incorrectly referring to the voltages as 208 and 480 Vac and see how well that is received. Also I think you are misinterpeting my use of the word "rack". I am not referroing to ladder rack used to support cabling. I was referring to telecom equipment racks, you know the aluminum or steel, 7' x 19" or 23" equipment racks used sometimes in telecom rooms and data centers that may be attached to metal cable tray or ladder rack. Do these need to be bonded ground? |
| | | | Forum Guru
       
Group: Forum Members Last Login: Sunday, February 14, 2010 10:27 PM Posts: 59, Visits: 249 |
| FL-RCDD (2/3/2010)
Thanks for your comments. I understand that technically 208 and 480 may not be the exact correct voltages. It has been a long time since I took three-phase power classe and it is irrelevant anyway in the discussion. I will be sure to let the PE, electricians, our DC manager and multiple manufacturers of UPS and computer room PDUs that they are incorrectly referring to the voltages as 208 and 480 Vac and see how well that is received. All I was trying to point out is if a 208 line were to fault to ground, the voltage is 120 to ground, phase to phase voltage is 208. That is why you will see in the specs 208/120 or 480/277. That tells you the circuit is 3-phase wye connected.
FL-RCDD (2/3/2010) l also I think you are misinterpeting my use of the word "rack". I am not referroing to ladder rack used to support cabling. I was referring to telecom equipment racks, you know the aluminum or steel, 7' x 19" or 23" equipment racks used sometimes in telecom rooms and data centers that may be attached to metal cable tray or ladder rack. Do these need to be bonded ground? Yes, it does not matter if it is cable rack or equipment racks, they have to be bonded.
DereckC MSEE, PEModerator Mike Holt Code Forum |
| | | | 
Forum Member
       
Group: Forum Members Last Login: Monday, January 17, 2011 1:25 PM Posts: 43, Visits: 158 |
| Whilst your all trying to create an unsafe environment for yourselves by not grounding all metalic components in a DC space. What do you suggest we do to dissipate the electrostatic build up that occurs in the space?
Steve Banks RCDDNightlake Ltd U.K. |
| | | | Forum Newbie
       
Group: Forum Members Last Login: Saturday, July 30, 2011 12:33 AM Posts: 3, Visits: 1 |
| | | | | Forum Guru
       
Group: Forum Members Last Login: Sunday, December 04, 2011 4:40 PM Posts: 64, Visits: 187 |