Grounding and Bonding in a Data CenterExpand / Collapse
Author
Message
Posted Monday, February 23, 2009 4:38 PM
Forum Guru

Forum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum Guru

Group: Forum Members
Last Login: Sunday, February 14, 2010 10:27 PM
Posts: 59, Visits: 249
Kevin J Article 645 is not a requirement; it is optional and rarely used. In fact most engineers and designer avoid like the plague due to the EPO requirements.

645 allows leniencies not otherwise permitted in the code and very strict requirements have to be met specified in 645.2 in order to qualify like the dreaded EPO.

DereckC MSEE, PE

Moderator Mike Holt Code Forum

Post #2807
Posted Monday, February 23, 2009 4:40 PM


Forum Guru

Forum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum Guru

Group: Forum Members
Last Login: Friday, July 16, 2010 9:58 AM
Posts: 93, Visits: 801
dereckbc (2/23/2009)
Kevin J Article 645 is not a requirement; it is optional and rarely used. In fact most engineers and designer avoid like the plague due to the EPO requirements.

645 allows leniencies not otherwise permitted in the code and very strict requirements have to be met specified in 645.2 in order to qualify like the dreaded EPO.

AMEN!

Doug Weis, RCDD, ESS

doug.weis@hei-eng.com

Post #2808
Posted Monday, February 23, 2009 4:40 PM


Forum Guru

Forum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum Guru

Group: Forum Members
Last Login: Yesterday @ 2:04 PM
Posts: 428, Visits: 2,196
dereckbc (2/23/2009)
Kevin J Article 645 is not a requirement; it is optional and rarely used. In fact most engineers and designer avoid like the plague due to the EPO requirements.

645 allows leniencies not otherwise permitted in the code and very strict requirements have to be met specified in 645.2 in order to qualify like the dreaded EPO.

Great, thanks Dereck.  Can you share links on subject?

Thanks,

Kevin J

 

A picture is worth a thousand words. 

Post #2809
Posted Monday, February 23, 2009 4:42 PM


Forum Guru

Forum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum Guru

Group: Forum Members
Last Login: Yesterday @ 2:04 PM
Posts: 428, Visits: 2,196
--

 

A picture is worth a thousand words. 

Post #2810
Posted Monday, February 23, 2009 4:52 PM
Forum Guru

Forum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum Guru

Group: Forum Members
Last Login: Sunday, February 14, 2010 10:27 PM
Posts: 59, Visits: 249
Kevin J (2/23/2009)
dereckbc (2/23/2009)
Kevin J Article 645 is not a requirement; it is optional and rarely used. In fact most engineers and designer avoid like the plague due to the EPO requirements.

645 allows leniencies not otherwise permitted in the code and very strict requirements have to be met specified in 645.2 in order to qualify like the dreaded EPO.

Great, thanks Dereck.  Can you share links on subject?

Thanks,

Kevin J

You bet I can here is two articles written by a close friend and ex employee of mine who designs data centers for a very large A/E firm who specializes in data centers.

645 Might Not Be RIGHT FOR YOU

EPO OR NO EPO

DereckC MSEE, PE

Moderator Mike Holt Code Forum

Post #2812
Posted Wednesday, February 25, 2009 11:48 PM
Forum Newbie

Forum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum Newbie

Group: Forum Members
Last Login: Saturday, October 29, 2011 1:59 AM
Posts: 9, Visits: 34
This presentation might help

https://www.bicsi.org/archive/2007MiddleEastDubai/12%20Panduit%20-%20David%20Hughes.pdf

Post #2846
Posted Thursday, February 26, 2009 11:42 AM


Forum Member

Forum MemberForum MemberForum MemberForum MemberForum MemberForum MemberForum MemberForum Member

Group: Forum Members
Last Login: Monday, January 17, 2011 1:25 PM
Posts: 43, Visits: 158
In the UK and most other European countries it is a requirement under the electrical regulations to ground all extraneous metallic items. Unless we start using plastic cabinets and frames then you must ground the cabinet.

Steve Banks RCDD

Nightlake Ltd U.K.

Post #2848
Posted Thursday, February 26, 2009 11:14 PM
Forum Guru

Forum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum Guru

Group: Forum Members
Last Login: Sunday, February 14, 2010 10:27 PM
Posts: 59, Visits: 249
sbanks (2/26/2009)
In the UK and most other European countries it is a requirement under the electrical regulations to ground all extraneous metallic items. Unless we start using plastic cabinets and frames then you must ground the cabinet.

Well that is certainly a requirement in the USA. But the questions/statement was:

"I am being told by a P.E. that it is not an NEC code requirement to ground equipment racks, cabinets, or cable tray in a data center with a dedicated grounding system  separate from the ground wire provide for equipment power. "

That statement is correct, but the engineer should have qualified his statement by saying assuming the equiment has AC powered equipment in it and electically connected to the frame.


DereckC MSEE, PE

Moderator Mike Holt Code Forum

Post #2858
Posted Monday, January 25, 2010 1:13 AM
Forum Newbie

Forum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum Newbie

Group: Forum Members
Last Login: Monday, January 25, 2010 1:09 AM
Posts: 1, Visits: 1
Hi All

Can somebody tell what is the name of BICSI data center paper and its schedule.



ADNOM Technology
Business Development Manager
Cell#: +92-321-2138599
Post #4365
Posted Monday, January 25, 2010 6:14 AM
Forum Member

Forum MemberForum MemberForum MemberForum MemberForum MemberForum MemberForum MemberForum Member

Group: Forum Members
Last Login: Monday, October 10, 2011 1:34 PM
Posts: 30, Visits: 78
I want to thank everyone for the comments.  Grounding and bonding is a fascinating subject but is probably the most misunderstood of all ITS topics.  I am still confused on what is / is not required in the DC by NEC and offer the following questions:

1)  If I build a data center with equipment racks /cabinets, cable tray and a raised floor with the intent of renting the space to co location tenants then do the metallic components need to bonded to ground if they DC does not contain AC powered equipment?

2)  What about racks / cabinets that are installed to support only cabling?

3)  If a fault current from an AC lighting circuit or other circuit was to energize metallic conduit, racks / cabinets, floor grid, etc without tripping a breaker and someone was killed from touching the now energized metal and if the family was to sue what would the court say in ragrds to NEC and who would be liable?

Post #4366