Which are the minimum requirements for build a Data Center?Expand / Collapse
Author
Message
Posted Wednesday, November 09, 2011 9:28 AM
Forum Newbie

Forum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum Newbie

Group: Forum Members
Last Login: Thursday, November 10, 2011 8:23 AM
Posts: 1, Visits: 5
I need to write a document where list the minimmum requirements for build a Data Center from scratch but does not know which are this requirements. I know TIA-942 (a bit) but this document is designed for "ideal" Data Center, any help on this?
Post #6611
Posted Wednesday, December 14, 2011 1:58 AM
Forum Newbie

Forum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum Newbie

Group: Forum Members
Last Login: Monday, October 29, 2012 4:57 AM
Posts: 4, Visits: 5
Read the following PDF. may be it helpful to you.


http://www.sans.org/reading_room/whitepapers/recovery/requirements-design-secure-data-center_561


Data Center India | Virtual Private Server | Dedicated Server India
Post #6759
Posted Tuesday, January 17, 2012 7:07 AM
Forum Newbie

Forum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum Newbie

Group: Forum Members
Last Login: Tuesday, January 17, 2012 7:01 AM
Posts: 1, Visits: 1
If you want to know more requirements about data centers take a look into this one. Its named as Colo-x.com. This is the best largest Data center.Colocation Docklands|London data center|Colocation Docklands



|
Post #6882
Posted Wednesday, January 18, 2012 8:35 PM


Junior Member

Junior MemberJunior MemberJunior MemberJunior MemberJunior MemberJunior MemberJunior MemberJunior Member

Group: Forum Members
Last Login: Monday, February 02, 2015 2:41 PM
Posts: 19, Visits: 77
Also check out the The Uptime Institute. They wrote the standard on tier data centers.

http://uptimeinstitute.com/

http://atd.uptimeinstitute.com/PDFs/TierStandards.pdf


Michael Russell, RCDD
michael.russell@graybar.com
www.graybar.com - Works to Your Advantage


Post #6893
Posted Monday, July 01, 2013 5:20 AM
Forum Newbie

Forum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum Newbie

Group: Forum Members
Last Login: Tuesday, October 29, 2013 5:00 AM
Posts: 4, Visits: 5
go4hosting is one of the best data center provider in India please contact him this will best for you..!!

they provides Dedicated Server India VPS Server India



Thanks Regards
Marshal Mathers

Post #8524
Posted Tuesday, January 21, 2014 12:57 AM
Forum Newbie

Forum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum Newbie

Group: Forum Members
Last Login: Tuesday, January 21, 2014 1:03 AM
Posts: 2, Visits: 4
As per my understanding on Data centers, The principle Requirement of a Data center is Management Softwares for maintainance and Data Center Racks - in which servers are placed.

Thanks,
Raj


Server Enclosures Manufacturers are very essential for networking business.
Post #8933
Posted Tuesday, March 18, 2014 8:26 AM
Forum Newbie

Forum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum Newbie

Group: Forum Members
Last Login: Friday, March 21, 2014 7:26 AM
Posts: 1, Visits: 5
Asia’s largest Tier 4 certified data center offering cloud server hosting, dedicated server hosting, VPS hosting and other data center services.
Post #9044
Posted Saturday, March 22, 2014 5:00 PM


Forum Guru

Forum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum GuruForum Guru

Group: Forum Members
Last Login: Wednesday, July 29, 2015 11:50 PM
Posts: 227, Visits: 858
My suggestion no matter DC size

1. Get all OPR. (Owner Project Requirement)
2. Get al GRC. (Governance / Risk / Compliance) premises
3. Define if:
3.1. Sustainability
3.2. Energy efficiency
Will be a premium drivers for the OPEration stage

Then set a conceptual DESign sent to CxA -Commissioning Agent). To be revise each assumption you have done. They must resend to you and you will have to update

4. So continue with each subsystem (at least)
- ARCHitecture & civil works
- COOLing
- ENErgy
- SAFEty
- SECurity
- IT transport

Finish all subsystems, cross pathways, spaces; set all Specs for bidding
Send again to the CxA. They must revise all your DESging is OK vs. OPRs
The Executive Project is ready to bidding stage

5. Then Owner / project director, can release the BID to tenders
5.1 The General Contractor (GC) & sometimes the subcontractors are appointed at same time

6. Project Director / Owner. Kick off the CONstruction stage
6.1. All incumbents keep the executive project and make any MACs to adjust real conditions. CxA. Revise this Updating to comply OPRs
6.2. All partial testing start
6.3. Project Director (PD) set the Final Test period before DAY 1 -in production-
6.4. CxA. Testify how PD & GC & SubC & OPE staff; made the component/systems/ total DC testings

7. All training to OPE staff in EACH and all systems is given
7.1.All technical documents. (Calculation, DWGs, technical and so on) have to been integrate, write, develop BEFORE the "handover" to OPErational Staff

8. CxA. Revise all procedures and documents to set to the Owner that ALL WPR have been fulfilled by GC, DESigner(s), all legal,technical documentation, training have been delivered to the owners' OPErational staff

Then Project Owner will sign the integral reception. It is common that bonds have been required to all incumbents to assure that any issue will be fix if arise during a time frame (most of the time 12months period).

This is a"simple" DC project no matter the size, cost, "T_ _R or location

Saludos
Roberto Sanchez, RCDD
México




roberto sanchez,RCDD
Perfil Activo y Creativo, S.A. de C.V.
México
Post #9054
Posted Thursday, June 18, 2015 5:15 AM
Forum Newbie

Forum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum Newbie

Group: Banned Members
Last Login: Tuesday, August 21, 2018 5:15 AM
Posts: 1, Visits: 4
Please take a look at Web Werks Data center . Web Werks is one the leading vps datacenter provider in India since 1996. We have evolved to deliver revolutionary products and services such as Virtual Private Servers, Dedicated Hosting, Colocation Services and Cloud Platform bundled with 24x7 Rapid Action Support.

Regrads,
Yesweb
Post #9842
Posted Wednesday, September 09, 2015 3:43 AM
Forum Newbie

Forum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum NewbieForum Newbie

Group: Forum Members
Last Login: Monday, October 05, 2015 5:41 AM
Posts: 5, Visits: 8
Requirements for a data center depends on type of data center - single-tenant or multi-tenant. Both have different guidelines. However, few of the common requirements for data center co-location facility are:

1. Power Infrastructure
2. Networking Infrastructure
3. Cooling Infrastructure
4. Security & Compliance
5. Customer Service & Support Staff

Here is one post discussing all these requirements in details - Essential Components of a Multi-tenant Co-location Data Center

Hope this post will help you to write a good paper on requirements of data center.


Olivia Grey
Data Center Specialist
Post #9993