| | Greetings, Please let me know if you have any reference document which would indicate the best practice for CAT5 patch panel. More particularly, I am looking for information on when a patch panel is required a) between 2 equipements in the same rack .. seems like adding 2 patch panel would be an overkill - please share your comments! b) between 2 equipments in 2 rack but in the same row of racks .. is there a limit of length to allow connection without patch panel? c) between 2 equipments in 2 racks but in different rows .. yes, the I suppose that in this case the 2 patch panels are required, but what I am looking for is a document to justify the cost of adding the patch panels Best Regards;  |
| | | | 
Forum Guru
       
Group: Forum Members Last Login: Saturday, June 11, 2011 9:29 PM Posts: 226, Visits: 844 |
| Just for Data Centres
if you are out from USA use the ISO 24764,
if in USA TIA 942 will enligth you.
saludos