| | Hello all, I am looking for the min. separation of conduits in a trench. My customer is having >5kVA electrical and UTP in the same trench and would like to know how far to keep them apart. Both will be in conduit. Thanks |
| | | | Forum Member
       
Group: Forum Members Last Login: Friday, October 08, 2010 5:40 PM Posts: 31, Visits: 517 |
| I believe the code in my area is at least 12 inches of separation from secondary electric power, when placing in a joint trench, and placing catv, phone, or data on top of electric power.
Future Technology Consultants
New York, New York |
| | | | Forum Newbie
       
Group: Forum Members Last Login: Friday, January 16, 2009 8:59 AM Posts: 4, Visits: 12 |
| smorse (4/15/2008)
Hello all, I am looking for the min. separation of conduits in a trench. My customer is having >5kVA electrical and UTP in the same trench and would like to know how far to keep them apart. Both will be in conduit. Thanks These are the required separations per the NESC: Separations Between Supply and Communication Conduit Systems Conduit systems to be occupied by communication conductors shall be separated from conduit systems to be used for supply systems by a. 75 mm (3 in) of concrete b. 100 mm (4 in) of masonry c. 300 mm (12 in) of well-tamped earth EXCEPTION: Lesser separations may be used where the parties concur. Regards, John Hamilton |
| | | | Junior Member
       
Group: Forum Members Last Login: Friday, February 03, 2012 8:53 PM Posts: 23, Visits: 34 |
| | Eric is indeed correct. Code says 12 inches minimum john adams |
| |
|
|